Rule ID: SUK/1017/2.3
This article describes the Fire Stopping Advanced Identity Rule that has been developed by Solibri UK Ltd as part of the BIM Coordination + Library.
The rule is used to identify where service penetrations occur with compartmentation walls and floors, along options for identifying both the presence of Openings, BWIC's / Fire Seals. It also ensures all service penetrations full penetrate both the compartmentation and are enclosed by Openings and or BWICs/ Fire Seals.
Penetrations detected between services and compartmentation walls and floors
This rule can be used for planning purposes at different stages of the project, determining where service penetrations occur, how many and whether there is a corresponding builder’s work in connection (BWIC), Opening or Fire Seal present.
This rule detects all service penetrations through compartmentation walls and floors. If a panellised floor system exists, a user-defined distance between those panels is considered to group them into a pseudo slab object. This object is then used, rather than the individual compartmentation components, to check for penetrations. This ensures penetrations through potential gaps or cutouts that reside between panels are not missed in the check. Where openings are created that produce no physical void geometry both in walls and floors the rule will still detect these instances, i.e. where no clash exists between services and either the compartmentation or the void geometry.
The rule first finds all penetrations of service components with walls and floors through their corresponding filters, then dependant on the options chosen, checks the presence of a Opening, Fire Seal or both. Other options check the service penetrates fully though and is completely contained within the Openings or Fire Seals.
The rule can be individually configured to give a single result, a selection or all the result types. The result issues indicate the type of failure (Based on option selection) for each of the individual service penetrations.
In the Rule Parameters view define the compartmentation, services and fire seals along with which case types you wish to identify. Alternatively use a predefined Common Parameter Name configuration to consistently utilise the same values for parameters within multiple fire stopping rules, essentially configuring the values only once.
Although this rule does not necessarily require the user to use a classification for each of the filters, it is good practice to use one for the filters in Rule Parameters as they will provide the following:
Help to structure the model geometry allowing easy identification and visualization in the classification of what will be checked
In subsequent fire stopping rules any services or fire seals will require classification values to interact with the FireStoppingRequirements.xlsx
Rule Parameters
Walls filter: The parameter table defines the compartmentation walls to be checked for service penetrations.
Floors filter: The parameter table defines the compartmentation floors to be checked for service penetrations.
Floor Distance: A distance value can be set so that floor components closer to one another than this value have their footprints combined to become a pseudo floor that is checked against service penetrations.
Services filter: The parameter table defines the services components that will be checked for penetrations that run through compartmentation components.
Service Merge Gap: Set distance to bridge and join gaps in services that would otherwise not fully penetrate the compartmentation component. Connections that terminate either at the edge or within the compartmentation may cause these to be ignored such as dampers that are connected to ducts.
Fire Seals filter: The parameter table defines the fire seal components assigned to service penetrations that should reside at those locations.
Fire seal depth reduced both sides by the Fire Seal on Wall Reduction Tolerance value - Used to ensure full penetration of services, not for other functions of the rule
Example Hollow Fire Seal
Result Options: 6 result options are available to filter the results
Show identified service penetrations that contains a fire seal and an opening
Show identified service penetrations that does not contain either a fire seal or openings (issue A)
Show identified service penetrations that contains an opening but no fire seals (issue B)
Show identified service penetrations that contains a fire seal but no openings (issue c)
Show service penetrations that does not fully go through its compartmentation or fire seal (issue D)
Show service penetrations that is not fully covered by its compartmentation, fire seal or opening (issue E)
Result conditions, passed and types A, B and C
Result issue types D and E
The rule results are arranged with two levels of categorisation. The first level categorises the floors where compartmentation have service penetrations. The second level then lists each compartmentation and its associated number of penetrations.
Categorisation indicating level and compartmentation and No. of issues in each
Each service penetration is assigned a number, then dependant on the option/s selected is then assigned the appropriate Issue code.
Penetration instance then prefixed with Issue type where appropriate
For illustration purposes you can see the associated results related to the activated options.
Colour Coded for illustrative purposes indicating specific penetrations and their issue type per compartmentation
Where individual options are checked i.e. multiple rules created to separate the different conditions these will all have the same issue type.
